SIME FORMAT HE COMBI , NO IGNITION (LOCK OUT)
Page 1 of 1
SIME FORMAT HE COMBI , NO IGNITION (LOCK OUT)
FAULT= spark but boiler fails to light , no gas.
assumed gas valve was faulty checked voltage from main pcb = 50 volts a/c ?.
the gas valve requires 240v a/c, at this point i was refering to manufactures to replace pcb,
but after speaking to sime , turns out smoke stat/flue stat was faulty ? simpley linked out and reset boiler and fired up 1st time , (240 v a/c at gas valve)
removed the link and replaced stat , jobs a good un!!